10,097 Registered Users
Topics7,432
Posts41,135
Members10,097
#40105 09/03/25 12:14 PM
Tac32 MRL with Bucher Valve keeps giving TSR fault
I have performed new HW scan.
I have tried the tsr magnet length adjustment. I have extended the slow down adjustment and changed following error. Might do it once a day or every run.
Anybody else fought this or have any ideas?
Have you measured your TSR magnet and input that value under P35?
Are you doing an SPC after changing P35?
Yes. Don't forget SPC. That's burned me before.
I’m not on site but I don’t recall seeing a TSR magnet. Where should this magnet be? The manual is unclear.
P35 is set to 0.1 right now which is what it was set to the day we walked on job.
TSR1 and 2 come in at the same time as NTST
Another Helper
Another Helper
Measure the selector tape magnets on back of tape on top floor. Need for P35 setting.
P35 = (length measured)
520 Offline
5 Offline
Change slowdown speed tac32, adjust car group,adjustment position system enter p17 for up p18 for down a good number is 1350 then hit enter go out to commands common to wrt hit enter Than RST the board, reset . It help me , after 2 week I change to 1250 and is working fine , original is 950 .my fault code was 1530.
For a 1530 you just need to pull the bottom slowdown magnet off and confirm NTS in the up still works.
I see this sometimes when there is too much magnet and I'll trim half off. Up fast monitoring and tsr1&2 need a little room.
You’ll get 1530s even without the TSR speed reduction for Endura with the P35 adjustment. The magnetic distances in the book are a bit too long. There’s even a bulletin on pulling the bottom magnet.
PHP: 8.3.37 Page Time: 0.038s Queries: 33 (0.012s) Memory: 3.0453 MB (Peak: 3.5946 MB) Data Comp: Off Server Time: 2026-11-25 01:59:59 UTC
