#40155 09/17/25 10:29 PM
6 stop Dover T4. Sent a learn trip and floor table looked good so saved the learn trip. When I put the car back to auto and sent a car call down the car ran down to the correct floor but at really slow speed, like even slower than inspection speeds. Then I sent a call up and it ran full speed. Back down - back to really slow speed. If it runs a full trip down the hoistway it will send a 981 or 980 error and a 17 for timeout.
Seems like the terminal slowdown switch is stuck high? But if I put that car on inspection, it will run at that super slow speed in both directions. Any thoughts on this? TIA
Need to run backup scan to setup nts/ets. Same menu you initiated hoistway scan