Posts: 118 |
We have a Kcm that hoistway access is not working when you key it onto access in the car it throws a 65 error and immediately closes the car door. Tried a new adon board and it does the same thing. Verified key switch wiring to the car too board and menu 4-1 says it’s on inspection but it will not run on access. Anyone ever experienced anything like this? Thanks
Posts: 280 Likes: 5
Posts: 280 Likes: 5 |
Did you check and or change the HAS board for that landing? If so did you do a lon download?
Posts: 227 Likes: 4
Posts: 227 Likes: 4 |
K442 Relay is de-energized for car to be on Inspection mode.
Controlling the K442 Relay is by switches on the ground side of the circuit.
K442:1 Relay is energized for car to be on Hoistway Access.
Posts: 270 Likes: 2
Posts: 270 Likes: 2 |
Have you checked 7-70 your top floor access #?. I had this change to 0 b4 by itself and an inspector came out and wrote it up. Wouldn't work.
Posts: 118 |
K442 is de-energizing and K442:1 is energized after keying the in car hoistway access switch. As soon as we do that the car is getting a 65 error and the car door powers closed. I’m thinking the LCE is not getting the signal from the adon card? Might try a new ribbon cable if I can get back over there today. 7-70 is set correctly and the route mechanic did try new has boards and performed the Lon download. 5-7-1
Posts: 800 |
The elevator thinks it is on cartop inspection, or MR inspection. Could be a wiring mistake. You may want to meter the inspection circuit with the wiring diagram.