1 members (sampler),
anger managment
anger managment
Posts: 31 |
(Txr5 with Vericon A/C drive) EVERY Monday morning at approx 4 am. And Now randomly during the week. I have 4car group shutting down at the same time with a Fault 10 FC Fault⦠we have had The building install a temporary voltage monitor for over a month and no power issues showed up.. I have changed all the LON and COM boards and swapped Gateway boards with no change.. I guess I can start swapping GCIO boards? I have spent countless hours trying to diag.. The only thing that works isā¦wait an hour or so, go eat lunch Come back and the damn things will work no issues!! š¤¬They will start working without doing ANYTHING.. They will start working as I am trying to diagnose them. I think I have them fixed but Noooo. EVERY Monday at 4 am they will fault out again. All the fault 10.. ANY ideas guys? Iām all out of ideas and so are the adjusters.š
Posts: 642 Likes: 5
Posts: 642 Likes: 5 |
The entire group craps out? Maybe something with EPO in the common panel:group controller? Tug every wire in the group controller and apply slight pressure to any pc board in that same cabinet and see if you getta change in modes. Is there a group status or monitor that shows on a screen what command is being issued at that time? Hopefully not āAutomaticā. Weirdly enough, years ago I had a group of trouble free Swift FUTURA cars that were adversely affected by a recently installed rooftop antenna (leased out rooftop space) that got its signal wires routed in a chase adjacent to the hoist way right where the DPP transducer was positioned on the crosshead. Somehow that close proximity of radio interference caused all kinds of issues.
What is the Fault 10?
anger managment
anger managment
Posts: 31 |
Frequency converter caused an emergency stop. VEC monitors SH contractor. If safety circuit opens, PVEC can detect this event before Travel Control does. Therefore, this event can also be caused by a safety circuit problem See measures and comments for SH_FAULT. Actions to be taken: - Look at Motor Control Event Log.
I have replaced SH contractor on all 4 units. No issues with the safety circuit. Believe me Iāve made sure all plugs are seated and wiggled every wire I can find trying to duplicate or prevent the problem. If one faults out and shuts down. They ALL fault out and shut down
Posts: 642 Likes: 5
No Emergency Power option on this group? Is so, disconnect the input signal or fuse that controls that input. Is this a new problem on the existing group? Any new construction additions to the building?
āFrequency Converterā fault sounds like incoming power especially as it affects all cars. Unless itās only the group controller that takes a momentary dump. Building Engineer doesnāt know of any changes regarding power like upgrading main switching gear etc?
Whose equipment is this?
anger managment
anger managment
Posts: 31 |
There is no Emergency power for this group. Thatās a good idea I will disconnect. Itās been happening for years but only happened a couple times per year. Now itās every week sometimes several times a week. There is remodeling going on almost year round. Several floors have been completed recently. I can disconnect emergency power connections easy Iāll try that now Itās Schindler Txr5 controllers No upgrades to main switchās
anger managment
anger managment
Posts: 31 |
I just disconnected Emergency power circuit. It was hooked up. But Iām šÆ sure these are not set up on emergency power. Now we waitš¤¦š»āāļøš
Posts: 642 Likes: 5
Yeah goofy stuff at times. Does the building use card readers or some other security feature? I only ask because they do interface with the group PB riser(s) and Fire Service which would affect all cars. Just thinking out loud and your ass is probably pretty sore by now so we want that to end as well.
anger managment
anger managment
Posts: 31 |
Well, itās not Emergency Power circuit. 𤬠All 6 units went down at the same damn time this morning at 1am They do have card readers. They all connect to a LON16 board inside each controller. I can start looking at that circuit.
Jacrispy
Jacrispy
Posts: 1 |
Posts: 805 |
Is there an earthquake input? Another possibility is some type of RF interference.
anger managment
anger managment
Posts: 31 |
I tried that. Ugh didnāt work. Went down again at 4am Thank you for the response
Posts: 642 Likes: 5
Well heck. The clues are;
All cars affected Early in the morning Becoming more frequent. Resets themselves which is super weird.
So hereās a thought; With the building engineer or managers approval, shut off Car 1. See what happens. Just leave it off (not on inspect or test mode but mainlined off) and let the other three handle dispatching. If the same outcome, try Car 2 etc until youāve proven itās not one car out of the four somehow pulling the group down. Could the Car thatās dispatcher, if it crapped out, send the same āFault 10 crap outā command to the others in the group? I dunno. Iām wondering about a group or individual car power supply issue where the voltage drops below or right at the operational threshold due to a flakey PS adjustable pot for CPU functions. Or- Is there an adjustment on the drive whereby you widen the time frame on this frequency fault 10 to offset false triggers or give more time before declaring the fault? Theyād all be set at the same default value Iād imagine. And that Fault 10ā¦itās the only logged fault with the same time stamp on each car each time right?
anger managment
anger managment
Posts: 31 |
Thanks for responding. I have done exactly that. Iāve been playing āmusical Elevatorsā for almost a year now I have shut all units down and tried to focus on just one. I worked on it all damn day today.. never could get it to come back up. Itās getting worse Iāve checked all power supplyās and adjusted to 24.5 volts And monitored voltage as the fault and shutdown happens. We are having electrician install voltage and amp monitors again for a couple weeks. The Drive throws an error 733 which is a ācurrent mains differentialā error. Itās just very odd it shuts down a 4 car group AND the same 2 cars in a different 3 car group like clockwork mondays between 1 and 4 am š¤š¤¬
Posts: 642 Likes: 5
Thereās an old thread on this site about the controller Txr5 and evidently thereās a SIMM card in the phone equipment Schindler uses. As the thread reads the controller can be accessed remotely and this āblock operationā can be induced like placing a car or cars on independent, lock out operation and adjust parameters according to one posters response. Iām wondering if this phone communication business has anything to do with your issues. Check out the thread. I found it doing a routine internet search and this site with this equipment popped up.
This is just flat weird.
anger managment
anger managment
Posts: 31 |
Thanks for the Response, We thought the same thing, and completely removed the modems and phone lines from all elevators. I will double check to make sure. There are 44 units total. These 6 units definitely have the phone modems removed. I canāt find that thread. But Iāll keep searching
Posts: 642 Likes: 5
Although your ass has been kicked for quite sometime on this job, youāre still at it, so congrats on that. Since these 6 units-two different groups shut down always on Monday early in the morning, these units are down until reset, or all 6 mysteriously recover on their own.
Any possibility you can have the building engineer (or yourself $$$) visit the site late Sunday and just key them down on Fire Recall (both groups), leave them and youāll return Monday as usual and see if the cars are faulted with the same fault? I mean, theyāre down anyways right?
Does the CPU on these units utilize a 5v supply or is it 24v? And does the fault description ācurrent mains differentialā have anything to do with incoming power phasing? Do the CPUās give more info on what happened when it happened? All I would want to know is if all units were idle when the command came to shutdown. Iām hoping yours were and you can prove it.
Typically early morning hours is when chillers, boilers or large cooling systems are brought up online for the day. If all drives fault the same when indeed theyāve been keyed onto Fire Phase 1 Recall (zero motion), Iād be inclined to point at incoming power and the drives detected the same incoming power issue in both groups. ***Both groups are in the same building?
Posts: 63 Likes: 1
Posts: 63 Likes: 1 |
Iād be curios to see the power analyzer results while these shutdowns are occurring. Seems like a incoming power issue.