Topics7,432
Posts41,135
Members10,097
Up then down
Up then down
Posts: 78 |
Tac 32 MRL will run for 4 hours or so and then starts stalling. Starts stalling about 2 foot out of the floor. IMS shows 1683, 1009, and 1040. THere is an occasional 1170. If car sits for extended period (thru the night) runs great again. Someone please confirm that MUTS (up to speed) comes in before UFS coil (up fast). Not clipping a door lock out of 1st floor. Note: This has had that environmental friendly oil that eats isolation pads, seals, etc for 10 years. We got the account a few months ago.
Posts: 647 Likes: 7
Posts: 647 Likes: 7 |
10 years running with that vegetable oil. Runs fine when cold. When you say the car is “stalling” out of the first floor (when hot I presume), does it MLT or just flat out drop high and run on level speed until the next landing? Other than you think it’s not clipping a lock, what are the fault definitions (1040)?
*Only occurs leaving 1st floor?
*Car toe guard or car sill nipping the interlock roller?
*Selector gets blipped or lost on a goofy misplaced magnet if it only happens leaving 1st floor.
*If it happens any floor going up, selector guides may be culprit (Oil/valve issue when HOT).
*If stalling without upward movement, packing might be suspect as oil can loose its lubricity and actually grab the piston in slowdown phase (Oil/valve issue when HOT).
Single piston or that telescopic type with sync sensors?
And IIRC, the MUTS picks then FST. If I got that wrong, IDWT will straighten me out!
Up then down
Up then down
Posts: 78 |
elmcannic Thanks.
Doesn't move from 1. Maybe a few inches. MUTS never comes in. Doesn't go on in up slow to intended floor. And IMS logs no fault?????
Only does it when hot or warm. If oil were to stay cool, it would keep running (long story but tested this). It does re level once in a while which is pointing to check valve(s) (man have we done alot of these check valves and have more lined up)
Bucher tool set on #3 at .02 (supposed to be within tolerance / hall sensor feedback). But now other techs are telling me that how tight the tank lid is affects this??? If something is that temperamental it shouldn't be in any elevator. Looked it up its true.
The last 3 faults are now this: 2766 1684 1170 in order (node comm, node comm loss or potential power supply, low pressure jack inhibiting down run). But my 20+ years doing this the 1170 caused it and the other two were the result in descending / ascending order whatever. But not sure how low pressure would cause comm errors.
Posts: 647 Likes: 7
MUTS never picks… So high speed valve coil won’t energize. Seimans Soft Starter? Failure of the control board for “motor up to speed” output was a big issue years ago with Seimans. Faulty MUTS relay? Does TK still use those 24v blue relays (about 10 of them) at the bottom of the 188E board? Those were valve control (VC) related. Back in the day we’d just replace an entire row when valve issues arise (shotgun for sure!).
But hot vs cool oil is still suspect and yes marginally sized oil tanks run hotter, and with the lid off, surface heat escapes. A fan blowing across the surface helps too in that case. Can you add new oil up to where car when in the dove tail (or at least resting on the springs) won’t spill over at the tanks feedline opening?
