Originally Posted By: Vsec
The drive was swapped with the unit next to it but not the resistors. There are four resistors that total up to 27 Ohms, the resistors read the same as the other unit, I've checked all of the parameters and they seem to be okay. The escalator does not get a full load every day where I can check the amperage draw of the motors. I'm leaning towards the resistors not being able to bleed off the the excessive voltage and current. I will try to go there soon and check on a couple of more settings on the drive itself. I would like to replace the drive with a re-gen drive.


If you have swapped the drive to the next esc and it faults the same it appears to me that you have transferred the fault next door. If the fault is exactly the same, then to me it cant be the resistors, motors(differing resistance) etc just the drive. So I would get the drive checked for that bleed off and try to get a new drive. You could swap the drive and leave them in place to see if the other drive effects the original esc for further proof if it doesn't fault out.