I am having an issue where this elevator appears to have a starting and running contactor (C1 and C2) C1 will pick, which appears to be starting. C2 will never pick. If I hotstick C2 , the motor will run at normal speed and make no noise. Otherwise motor almost sounds like it is single phasing. I have no prints so I am pulling wires to try to figure this ckt out. Does anyone know it that well or have a print? It is a Type AC391E No. 925 220V single Phase.
|
|
|
|
|
Joined: Jan 2014
Posts: 141
member
|
|
member
Joined: Jan 2014
Posts: 141 |
Not familiar with Shepards, but commonly find the aux. contacts not making on first contactor.
|
|
|
|
|
Joined: Feb 2013
Posts: 800
old hand
|
|
old hand
Joined: Feb 2013
Posts: 800 |
not familiar with Shepard either, but some companies picked both contactors at the same time so if one were to weld in the other would drop out, and indeed it is single phasing. Have you put a meter on the coil wires of the contactor that isn"t pulling in?
|
|
|
|
|
Joined: May 2011
Posts: 487
addict
|
|
addict
Joined: May 2011
Posts: 487 |
I'd start with a meter on C2 then try pulling them back, maybe a timer not working properly.
Last edited by E-man; 08/02/14 02:00 PM.
|
|
|
|
|
|
|
|
|