Uppo.. it is a single car.
At this point.. I would love to be back to the over speeding problem!! I have been battling with the new generator set up that seems to be a never ending night mare. Here is what it is doing now.
The unit will run fine in the up direction with out over speeding.( Have not put a tach on it but it does not trip the gov. switch)
When you put in a down call the gen loads up and wants to shut down, and the motor stops turning. It burned up the DF Coil in the leveling field, I assume because I didn't kill the power in time. I am getting the same field motor voltage and armature voltage in both directions as well as the same GLF voltage to the gen.
It will run down on inspect and if you run it up on inspect the motor at first jumps a couple of times and then smooths out.
On automatic if I block out the speed switches(which I assume is blocking the loop circuit of GF and GF1) and put in a call it will run down on slow speed until it comes in to the called floor and then will not level in. Talking to the motor shop he suggested I swap GSF and GSF1. Tried that.. no avail. He then suggested to swap GA and GSF around and it tried to load up without a call on it. The last suggestion he gave was to hook up GSF2(which is not hooked up to anything) in the place of GSF1 and leave GSF1 unhooked. This did not make any difference.
Thanks to everybody for your suggestions and help.
Thanks for your reply. We do have to clarify some points ie --when you put a down call and the gen loads up- does this trip the o/l and is that what you mean by wants to shut down?
--in this instance what do you mean by the motor stops turning?
--have you actually re-wired the genny? Changed anything settings/taps but have put them back? Set your neutral plane back to where it was, as its most likely they will be ok if it was working fine before.
Ok I think you need to prove that your hoist motor fields are indeed of the same value as if they aren't, then it all wont work. Also check that the field is replaced/repaired in the right polarity(no wire cross over, cross over etc). As to your stepping when on inspection the lifts gets jumpy, I would definitely check your U,UX,D,DX,1E contacts and brushes, plus their leads(most important) to make sure no high resistances or breaks under load are present.
When the lift tries to run on inspection on the up, does this stutter occur in all places in the shaft? Is it better down the bottom or up the top? What about the down?
As to your running the lift with your speed switches out, which lets full resistance in the GSEF and loop circuit, when it cant level in, is the lift stalling? Have you tried to push in the D contacts in the GLF circuit? What about DX in the loop circuit( or the diode)? I have also read somewhere that you should tune your empty car compounding via HSL speed with the up direction a little faster than the down. At the moment lets not get that deep yet. Also check your suicide circuits as well.
Any way this is just some thoughts to consider.