Check addresses at I/O 1-12 (car calls) then
check addresses at I/O 161-172
(card reader inputs)
They will need to be different from each
other. You will need to change binary
address of the board used for card
reader inputs to 16 if it's set for 8
because car calls (I/O 1) typically
start at add. 8-2 and card reader inputs
(I/O 161) typ. start at add. 16-1. You need wires
from card reader relays to inputs according
to your wiring diagrams. Set en-crc
parameter in group 7 to a type 7 or 8. This is
the proper way to set up card reader.