16.1.3 Setup drive (5 _2 _ 1)
Step Action Note
1 Ensure that the elevator is in RDF.
2 Position the car with RDF so that LEDs 61U, 30 or B30 (or both), 77N and 77S are
lit.
3 Reset the earlier floor settings:
1. Select Menu 6 with MENU
button.
� Press ACCEPT to
confirm selection.
2. Select submenu 6_16 with arrow
buttons.
3. Set value of parameter 6_16 to 4
with arrow buttons.
� Press ACCEPT once to
confirm selection.
4. Recycle power.
On display:
6 _ 0 _ n, where n is the ID of the
parameter sheet.
6 _1 _ _
6_16 _ 0
6_ 16 _ 4, where all numbers are steady.
4 Activate shaft setup menu:
1. Select menu 5.
2. Select submenu 2.
3. Set the value to 1.
On the display:
5 _ _ _ _
5 _2 _ _
5 _2 _ 1
5 Start the setup drive:
� Turn RDF (270) OFF (to normal).
Car starts to drive in up direction.
6 Follow the run in the LCE User Interface.
If the elevator does not start to drive:
1. Safety input LED is lit in the LCE User Interface. If not, check that if:
� the car is at limit switch
� safety chain is broken.
2. Check that value of the elevator mode parameter 4_1 is 0.
� If the value is something else than 0:
� Check all the key switch settings (FRD, PRC/L, OSS, e.g.),
� Settings on LCEOPT board
� Commands from group control (should be disconnected).
3. Check that the car light supervision parameter 1_77 is 0.
4. Check the doors
� No doors open
� No photocells active
� No door open buttons active
5. Reset faults and do the floor learning run.