#18116 09/24/16 12:49 AM
Joined: Mar 2014
Posts: 23
G
Luv t o Brew!
Luv t o Brew!
G Offline
Joined: Mar 2014
Posts: 23
Hi, coworker has a nagging issue with a TAC 32. It shuts down every couple days with a low oil fault. Seems to only happen overnight. We adjusted the valve for proper leveling distances and speeds. It's a I2 valve, by the way. We also cleaned the strainer on the valve to eliminate that as a possibility. Obviously, we checked the oil levels and made sure no cavitation was occurring. Not sure what we are missing. Could it be running on viscosity and not bypassing the low oil timer during it? I don't have any 32 on my route so these controllers, although look similar to the 20 and Icon, seems to have quite a few differences. Also looks like it has a few proprietary peculiarities that I am not privy to. Just navigating he LCD screen was frustrating. Any ideas would be appreciated.

gandye92 #18117 09/24/16 12:55 AM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
What fault code specifically is it getting?

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
I ask because the 1043 is the standard low oil shutdown but I have had problems with the Z44 adjustment causing 1123 Up run stalled faults. Sticky packings can cause this but more than once I have had to reload the software because no matter what I set Z44 to, typing Z44 in remote fast would return Z44=0. I think that fault was a Run Monitor though.

Joined: Feb 2012
Posts: 82
N
journeyman
journeyman
N Offline
Joined: Feb 2012
Posts: 82
If the car is relevelling quite often while static, leakdown back into tank or leaky packing, you might ocassionally have a contact failure for the low speed valve causing the car to time out since motor is running but valve is not opening. we have seen this a lot with constant relevelling every few minutes on Tac 20. All the best!

NY Guy #18126 09/24/16 02:44 AM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
There are no relay contacts in the valve coil circuit on a TAC32 and it monitors that there is voltage on the coil.

Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
See if your coworker can view the position count while the car is in viscosity mode. If the low pressure setting is wrong, the car will creep up, level back down over and over. Or, disconnect the hi/low temp wires for a period of time and see if the trouble disappears. And it never hurts to check the low oil timer setting.

elmcannic #18134 09/24/16 03:48 PM
Joined: May 2011
Posts: 338
A
ABE Offline
Mechanic
Mechanic
A Offline
Joined: May 2011
Posts: 338
Never try to clean the screen on your up leveling adjuster On the I2 and I3 valves...just replace it. The screen is too fine to accurately clean. A dirty leveling adjuster can can even cause LOT to intermittently fire or the car can stall all together.

ABE #18135 09/24/16 04:30 PM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
I would 2nd that. By a mile the most common cause of any up issues in an I-2 or I-3 valve. Always have a spare and clear O-Rings, replace the O-rings if the adjuster can be turned by hand, and PLEASE, Never remove the screen!

Joined: May 2016
Posts: 4
R
stranger
stranger
R Offline
Joined: May 2016
Posts: 4
I'd try keeping it simple and if you've replaced the up leveling screen, you might take a look at the other screen that is located underneath the up pilot block...we had a lot of these getting clogged after construction due to lint ( running a rag thru the pipe to clean it)
good luck

railbug #18137 09/24/16 10:13 PM
Joined: Mar 2016
Posts: 270
Likes: 2
L
Elevator guy
Elevator guy
L Offline
Joined: Mar 2016
Posts: 270
Likes: 2
Try tweaking the up slowdown in just a fuzz had a few stall out and that took care of it, check leveling speed first

lowoil #18139 09/25/16 08:18 PM
Joined: Mar 2014
Posts: 23
G
Luv t o Brew!
Luv t o Brew!
G Offline
Joined: Mar 2014
Posts: 23
Great tips guys! I will relay this information to my co worker and I will report our success. He already disconnected the cold temp thermostat. If it runs for a couple days that will narrow our search.

gandye92 #18193 09/28/16 09:54 PM
Joined: Mar 2014
Posts: 23
G
Luv t o Brew!
Luv t o Brew!
G Offline
Joined: Mar 2014
Posts: 23
Ok so it turns out the the relief pressure was t set correctly. It was set to bypass at around 200 but was supposed to reach 305. It was prolly stalling at night when the cleaners were loading up their carts or whatever. You have to put your detective hat on when diagnosing these problems I have come to realize. Anyway, the elevator is coming up to speed nicely and after some adjusting all the floor levels and approaches are perfect. This was something we hadn't considered given the elevator had passed inspection and was sealed. Just proves that you can't assume things and take things for granted I suppose. We haven't had the elevator running for long but I am confident this was the issue with it.

Last edited by gandye92; 09/28/16 09:55 PM.
gandye92 #18195 09/28/16 11:36 PM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Nice work! Thanks for the update.

Joined: Mar 2014
Posts: 215
S
enthusiast
enthusiast
S Offline
Joined: Mar 2014
Posts: 215
Those numbers sound low. I do a lot of tac32H elevators and typical no load pressure is 160-180, with a full load pressure around 320-360. Typical relief is set in the mid 400's to the low 500's.

Silly #18446 10/24/16 02:27 AM
Joined: Oct 2016
Posts: 42
P
newbie
newbie
P Offline
Joined: Oct 2016
Posts: 42
I would agree those pressures seem low. Is this a twin post telescopic?


Philelevman
Joined: Mar 2014
Posts: 23
G
Luv t o Brew!
Luv t o Brew!
G Offline
Joined: Mar 2014
Posts: 23
Just checked this post. I will look into these numbers and update the situation.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.029s Queries: 46 (0.009s) Memory: 3.0719 MB (Peak: 3.5927 MB) Data Comp: Off Server Time: 2026-09-21 07:17:13 UTC
Valid HTML 5 and Valid CSS