As its running the scan I'm sure it's logging a 118 fault at each floor. I noticed today that it had a 118 6010 at all floors but the 2nd where it had a 118 6011. All the magnets are the same length and I've checked to see if rail was magnetized and it was not. Brg, you mentioned that a v3f25 should not have sensors and magnets for leveing. I wonder if this unit was altered for some reason and it's had this issue ever since. It just doesn't make sense how it's supposed to be able to do a floor scan and then be able to relevel properly with the system of sensors and magnets acting like they are.


If all else fails, read the instructions