Hello all,

Has anyone experienced a car call button acknowledgment light that didn't cancel on these units?
It's only 1st floor and I changed the (K2EB) I/O board (Part #ABA26800AHE1) that it plugs into with same result. Button works fine. Able to move problem to any call button.

Also on the same car the Fan & Light Protection relay (FLPR) picks up instantly and won't drop out to allow car lights to turn on. Changed CIRS board (Part #GDA25005B1) and no change.

Any help at all is good help. Thanks for reading this.

Joined: Jan 2014
Posts: 432
addict
addict
Joined: Jan 2014
Posts: 432
did you try a pf ram reset m151? had a car gong that would not turn off, went down the same road as you replaced boards etc. same thing did a m151 and problem cleared. also there was a problem with flpr as well. m151 corrected them both.

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
I did the only ram reset I know of. Car on inspection, scroll with S2 button to function 6. Scroll through to CLRO and hit reset to clear BAT RAM. Is this the same as m151?
Cleared this way a few times with no luck.

Thanks for the response.

Joined: Jan 2014
Posts: 432
addict
addict
Joined: Jan 2014
Posts: 432
hmm not sure, usually just use the tool, not the onboard interface. sounds similar, except the tool says PF power failure ram reset. and onboard says BAT ram reset.? not really sure, but it seems similar. any way to access a tool? just to check it out. maybe a otis guy will chime in good luck keep us posted

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
Nope, no tool. Haven't needed one till now I guess. Does sound like the same function though and I see no other type of reset mentioned in the manual. Really appreciate you getting back to me.

Joined: Aug 2016
Posts: 778
J
old hand
old hand
J Offline
Joined: Aug 2016
Posts: 778

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
2nd that. Best $100 I ever spent.

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
Gentleman, you convinced me. Just ordered one. Have more then enough 211's to justify the purchase. Thanks.

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
On board bat ram clear and svt m151 clear should give similar results . If you changed the button and the remote station and still have it then it could be a problem in the software where the output for the tell tale light is permanently on . If you get yourself a service tool check the I/0 state , it should give you the I/o number in the prints I've had this fault but its been the behind COP remote station ( KEB ) board everytime . The light and fan relay is a changeable setting from the last run and can be changed with a SVT .

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
Did you inherit the fault or has it appeared suddenly ? If like it when you took the job I would say its like the car button tell tale is addressed wrongly

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
When you get the svt check car serial address 34-1 for the CCB01
Input is the button output is the tell tale light . On SVT go 1 (ocss) 2 (test) 1 ( RSL I/O ) then it differs on vintage I believe but it may say c equals 1 h equals 2 g equals 3 . If so press 1 . Type in 34 press blue and enter , it will show input output state for 34 bit 1 which is 1st floor button and light . ( if u want to check floor 2 press blue and up to change the bit to 2 again to 3 etc etc ) check the output is OFF if no call registered . If on when no call is registered try turning it off from the SVT press blue and zero until it changes to off then go and see if it extinguished. For some reason on the one in looking at right now if you activate the button while looking at input output state then you HAVE to turn it back off from the tool . Pretty sure thats the case for all. Try this and let us know . Hope it helps .

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
UPDATE....
So this is weird , just the process of me going into the RSL I/0 ended up replicating your fault. It was fine for a time as I was checking etc.. When I went to leave I Locked up called the elevator up and the fan and light where out and when you register a call on any floor it does not extinguish the lamp after answering . Even weirder is the fact that I went back to machine room plugged my SVT in and as soon as I did the flpr relay picked and the fault whent away. Try M-1-5-1 as vatorgator suggested before anything .

Joined: Jan 2014
Posts: 736
R
old hand
old hand
R Offline
Joined: Jan 2014
Posts: 736
If you do M-1-5-1 use clear PF Ram not Clear SAC RAM.. Sac is for car button secured floors.

Joined: Jan 2014
Posts: 432
addict
addict
Joined: Jan 2014
Posts: 432
hey pieman, i have experienced strange results from playing with the tools on the rsl I-0's
i think i have posted and had some responses on this forum. anyway being curious while working on some 211 hydros, i would try and turn on certain outputs just to play around and see if i could get it to work, strange thing is if you try and turn on a output from the tool, lets say fireman jewel, for example. i would try and it would not turn on, then i would stop playing, and get ready for next service jog, when about to leave i noticed the first floor hall button would not extinguish. had to do a m151 pf ram reset. did not think much about it, but i have played with it on various 211 controllers, and as soon as you get into the rsl io section and try to force an io, then strange things happen. it does not go as the manual says it should. been down this road a few times,

Joined: Jul 2013
Posts: 206
N
enthusiast
enthusiast
N Offline
Joined: Jul 2013
Posts: 206
Most Otis controllers respond similarly when manually toggling I/Os.

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
Yeah , I tend not to toggle I/o's unless specifically trying to prove something ,had some spare time so was playing around. Funny it created the exact same fault including dropping the light and fan relay.did not even have to do a PF ram reset to clear the fault just plugged my service tool in and hey presto. I look after a lot if 211's and thought I had seen everything , guess not .

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
Wow, Thanks for all the help. Haven't checked in a few days. Still waiting for the tool but, did not inherit the problem and the original problem was the flrp relay staying picked. No car lights. The halo not canceling popped up while trying to figure that out. Off next week but tool should be here upon return and I try all your suggestions. Hope it doesn't take too long to figure out the tool. I ain't no kid no more!!

Joined: Aug 2014
Posts: 106
P
member
member
P Offline
Joined: Aug 2014
Posts: 106
The light and fan relay and the halo not canceling seem to be related . That's what I had . First thing to do is plug in your tool, press module - 1 -5-1 and blue enter for PF ram reset ( as someone else said don't reset the SAC ram ) . Good chance that will do it .

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
Thank you very much.

Joined: Dec 2012
Posts: 23
F
Liftfixer
Liftfixer
F Offline
Joined: Dec 2012
Posts: 23
So, back from vacation. Got the Tool. Went to 3 different 211's today and got the same thing. Plug it in, get start up logo then it changes to press module but just as quick StStStStStSt (self test I assume) starts filling up the whole screen and won't change. The manual I've been able to attain shows a SELF TEST mode first but nothing about what I'm getting. If I press the blue shift key I'll get software version and date but nothing else.
Just wanted to see if it's me or the tool before I contact the seller.
Thanks for any help.

Page 1 of 2 1 2

Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.028s Queries: 54 (0.010s) Memory: 3.1174 MB (Peak: 3.5927 MB) Data Comp: Off Server Time: 2026-09-20 12:32:41 UTC
Valid HTML 5 and Valid CSS