LRV4 non enhanced.
3stop
happens at all floors.
Have discharged SuperCap.
Problem returns immediately.
Doors will close after car call is pushed and door close button is pressed.(this symptom has changed in varying degrees)
Monitor all inputs at board. (electronic edge, DOL, DOB ,old safety edge input all working normally.)

Changed Hall Interface board due to another symptom. New board did same thing.
When the units gets to top floor(3rd) led lights(3U,HPI1,HPI4,4D,HPI3,4DL,3DL,1UL) all light up.
The hall pi lights are reading correctly, and 1 up light isnt physically on.
All hall buttons work normally and will answer call and cancel once the elevator is moving.
Discharging the Super Cap is the only way to get rid of led's. Comes back once it hits 3.

Have monitored the position inputs(OK), all PI's working correctly

CPU on its way, just wondering if something else could be causing this.