#24618 08/28/18 12:53 PM
Joined: Jun 2017
Posts: 36
N
newbie
newbie
N Offline
Joined: Jun 2017
Posts: 36
Crew was in doing annual testing and performed a low oil test. The test was successful but now elevator will not run up or down on automatic or inspection. When on automatic I can place a car call and y delta pull in properly and the pump turns on but not getting the coils to pick up on the maxton valve. Coils have been checked for resistance and are good. On inspection the pump dose not turn on at all. No prints on site and not sure where to go from here. Any ideas would be greatly appreciated.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
Is this relay logic, or Miprom?

Joined: Jun 2017
Posts: 36
N
newbie
newbie
N Offline
Joined: Jun 2017
Posts: 36
Relay logic. Also would like to know what the to set the UST and TS timers too?

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
If this is a relay logic, do you have a BOR relay? It is energized on start up to bypass oil. If the TA Timer is bad or a contact on BOR is bad it will bypass. Not running on inspect, you probably have a bad INS relay, or contact.

Joined: Jun 2017
Posts: 36
N
newbie
newbie
N Offline
Joined: Jun 2017
Posts: 36
I don’t have a BOR relay on this controller. I went ahead and ordered new timers as these look original and see what happens from there.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
K, let me know.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
UST is the up stop timer. It runs the pump momentarily after you stop leveling. Set for 1-2 seconds. The TA is the WYE/DELTA transfer timer, so 2 or 3 seconds or so.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
TS is the up and down stop timer, it works with the door open and close times.

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
If you give some more info I’ll see if I have a close print. Passenger or freight? How many stops? Selective/collective? Does it say SPM on the controller?

Joined: Jun 2017
Posts: 36
N
newbie
newbie
N Offline
Joined: Jun 2017
Posts: 36
Gentlemen, first off thank you for your quick response to my issue. We replaced all four timers to be sure that they were functioning properly and still had no luck. We then found out that the overload was changed out by a mechanic one night just before the crew were sent in to do the annual testing and the wires that go to the one normally open and the one normally closed were switched around. Once they were put on the proper contacts we were up and running again!
Once again thank you kindly!

Joined: Dec 2017
Posts: 37
H
newbie
newbie
H Offline
Joined: Dec 2017
Posts: 37
I have to ask this question. How was a safety test successful if the elevator didn't run?

Joined: Jun 2017
Posts: 36
N
newbie
newbie
N Offline
Joined: Jun 2017
Posts: 36
They pulled the coil wire off the up fast coil then placed a top floor call. Y delta pulled in pump would run then PT timer would time out doors would open and close like they should. The thing is pump was just bypassing and it never even left the bottom floor.

Joined: Oct 2013
Posts: 120
C
member
member
C Offline
Joined: Oct 2013
Posts: 120
This is why we need witness testing by inspector.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
Sad to say your right. Although bypassing sounds a lot like the relief, it is not the same. You have to ask if a gauge was in the system to show static then relief. My guess is Not.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.027s Queries: 42 (0.009s) Memory: 3.0615 MB (Peak: 3.5927 MB) Data Comp: Off Server Time: 2026-09-20 20:16:59 UTC
Valid HTML 5 and Valid CSS