Hi guys. I got a tac 32 shutting down almost every morning with 2 faults 1110 - A17/B44 shutdown 1074 - jack low pressure shutdown
When this first happened I replaced the up leveling strainer and we had no problems for 10 days or so. Now it’s happening almost every morning. I adjusted the slow down on the valve body . But it is still shutting down. Any ideas as to where to look next ?
Make sure z44 is set to 100,did you turn in on the up slow down? An 1/8 or 1/16 turn in will stop those early morning stall outs.also check leveling speed after messing with up slow down .only seen this on brand new jobs dont remeber if it had the 1074 tho.
Have problem with a tac32 hydro duplex . Only one car picks calls. The other has ebad light blinking. Could this be the problem ? What doesit mean.ITS MY FIRST TIME WITH THIS TYPE OF CONTROLLER
You may need to Update your software I believe some older versions of the software have this low pressure problem but only during a jack resync. Do a FJR see what happens