Who's Online Now
0 members (), 31 guests, and 1 robot.
Key: Admin, Global Mod, Mod
September
S M T W T F S
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29 30
Newest Members
Josephs, Javy89, Ropeguy67245, kywewa, Ingvar
10,040 Registered Users
Forum Statistics
Forums13
Topics7,385
Posts40,939
Members10,040
Most Online3,137
Apr 9th, 2026
Previous Thread
Next Thread
Print Thread
Joined: Jan 2011
Posts: 119
S
Shootintrouble
Shootintrouble
S Offline
Joined: Jan 2011
Posts: 119
Have a Kone KDL16 giving us hell. These are the symptoms:

Run on inspection up or down brake and ebrake picks
Car shutters floats and drifts up slightly. 102 flt xtra 2002.
Drive has been changed with known good drive from elevator in bldg. Motor encoder changed with known good encoder from same running elevator in bldg. LCECPU and Adon both from running car. Drive setup 6_60 = 10.25. Also tried setting the drive up with custom motor nameplate data 6_60 = 88.88. Loadweigher is at 0% empty car. Main line voltage is at 490 vac tapped to a step down transformer 415 vac to the kdl16L drive. Motor phase to phase is .2 ohms. Phase to ground = O.L. This elevator will run open loop just fine 6_65=0, but if you Choose 6_65=-2 or 6_65=2 car shutters, floats and drifts up.

Any ideas?

Joined: Nov 2018
Posts: 2
V
stranger
stranger
V Offline
Joined: Nov 2018
Posts: 2
Probably the Stator of the Traction Motor

Joined: Jan 2011
Posts: 119
S
Shootintrouble
Shootintrouble
S Offline
Joined: Jan 2011
Posts: 119
Thanks for the reply. Meaning stator is bad or I need to change the stator resistance parameter? The machine will pick the brakes and try to drive down on inspection with a down run but just floats there then faults out with the above fault. The drive is outputting 127vac phase to be phase while trying to drive on inspection.

Joined: Apr 2016
Posts: 27
L
newbie
newbie
L Offline
Joined: Apr 2016
Posts: 27
Motor leads U V W. Is W from the motor hooked to W on the drive?

Joined: Jan 2011
Posts: 119
S
Shootintrouble
Shootintrouble
S Offline
Joined: Jan 2011
Posts: 119
I believe so, but I’ll need to verify this to be 100%.

Joined: Jan 2011
Posts: 119
S
Shootintrouble
Shootintrouble
S Offline
Joined: Jan 2011
Posts: 119
Motor is hooked up right. I’m truly believing we have a bad MX 10 motor stator. During a high current demand with an initial start up the machine simply cannot perform. I noticed today that the voltage never breaks past 60vac phase to phase as compared to another working machine which ramps up from 0vac to 250 vac on inspection. When running open loop it runs okay because it ramps up faster and sharper. Even in open loop there is a bad shudder until it breaks over the 60 vac threshold. With the encoder hooked up it never gets past the 60vac then throws a drive over current flt. I’m thinking the windings in the stator are failing when the current demand is high. 60vac to start the elevator acceleration and to get over the inertia of moving the load.

Next step here is going to be land the car, getting the ropes free and run this unit unloaded. If it runs with no load in the same setup I’m pretty sure it’s the motor.

Still looking for ideas if you have them.

Joined: Jan 2011
Posts: 119
S
Shootintrouble
Shootintrouble
S Offline
Joined: Jan 2011
Posts: 119
Bad new motor encoder from Kone. Read good on O-Scope but for some reason did not work when hooked up. Installed another new one from Kone runs like a champ. $2k later.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.025s Queries: 28 (0.005s) Memory: 3.0271 MB (Peak: 3.5921 MB) Data Comp: Off Server Time: 2026-09-21 00:44:02 UTC
Valid HTML 5 and Valid CSS