Have a 682,981,1683 faults that shut the car down at same floor 95%of the time.Checked power supplies raised them to 24.4 no help checked lock contact needed better wipe fixed that.Gov encoder looks good an tight could this drive shut down be caused by a door lock or operator issue.Also checked hoistway vane engagement plenty of bite on vanes.Car might run hours to days before shutdown but recently daily.
|
|
|
|
|
Joined: Dec 2015
Posts: 1,769 Likes: 12
ElevatorPractitioner
|
|
ElevatorPractitioner
Joined: Dec 2015
Posts: 1,769 Likes: 12 |
|
|
|
|
|
Joined: Jan 2014
Posts: 132
member
|
|
member
Joined: Jan 2014
Posts: 132 |
|
|
|
|
|
Joined: May 2015
Posts: 359
enthusiast
|
|
enthusiast
Joined: May 2015
Posts: 359 |
Car Fault: 682
Fault Description:
Encoder Alarm Fault - The encoder returned an alarm bit, indicating a internal problem which is either with the power supply to the LEDs in the encoder, or a faulty position reading in the encoder.
Possible Causes:
Noise
Internal encoder failure
Possible Solutions:
Verify that the P5 VDC supply at the Absolute Encoder Interface Card (6300RC2) is no greater than +0.05 or less than -0.0 with respect to test point DGND on the 2407MC card
Verify that the P5 VDC supply at the encoder interface card (6300XA1) is no greater than +0.25 or less than -0.05 with respect to G5 terminal on the card
To Reset the Encoder Alarms
Access the Drive CMD Menu
Arrow down to View Alarms
Press Enter to reset the encoder alarms
|
|
|
|
|
Joined: Dec 2015
Posts: 1,769 Likes: 12
ElevatorPractitioner
|
|
ElevatorPractitioner
Joined: Dec 2015
Posts: 1,769 Likes: 12 |
I doubt it’s door related but it doesn’t hurt to make sure DCL6 is set correctly. Some of these encoder faults can be hard to track down, especially on the 10K drives. First you have to rule out any shielding problems. I forgot to ask if it’s a PM motor. Assuming it is, the drain is in the encoder. So do shield wire lands to interface card at motor, no tail out to ground. Make sure the shield is not landed in the machine room on the RC2 board. If it is landed to the RC2, it can be ok if the Faston terminal is not grounded but best just not to land it in the MR at all. Machine grounding is also important since the encoder drain is through the machine.
|
|
|
|
|
Joined: Jan 2014
Posts: 132
member
|
|
member
Joined: Jan 2014
Posts: 132 |
Been out for health .But my back up called said he swapped power supply from other car in group an hasn’t had shut down yet,power supply is the drive Ps
|
|
|
|
|
|
|
|
|
HW PM
by Chris, January 13
|
|
|
|
|
|
|
|
|
|
|
|