Looking for some help on a vertical express 2 stop hydro.... tried calling tech support for this and was told they won't help because we are not Thyssen techs.

During our recent state test during the fire service portion the inspector discovered a problem. Capture the car using the hall fire key, turn car on to phase 2 in the car and take it to the next floor up...all working good. When we turn the fire switch in the COP to the hold position it will not take calls and will sit with the doors open which is correct. The problem is that when on hold the door close button should be disabled however if you press it the doors will begin to close - it is constant pressure so if the switch is in the hold position and you press and hold the door close button the door will fully close. Once fully closed if you release the button the doors remain closed, if you press the open button the doors will not open. In other words on fire phase 2 with the key in the hold position, someone could theoretically walk into the car and hold the close button until the doors fully close and then would be trapped inside. as a result the elevator was shutdown and as i said a couple of attempts to get tech support on this have been useless. I believe this has been this way since original install since this inspector is a new guy and pretty thorough to say the least so in the past it has never been picked up. Thinking its a programming issue, all other functions of fire service work properly.

Hoping someone might have some insight on the issue, where and how to look/change any type of programming if needed or possibly send along a contact that is willing to troubleshoot this with us.

Thanks

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Is it a Tac-20?

Joined: Nov 2009
Posts: 468
Journeyman
Journeyman
Joined: Nov 2009
Posts: 468
Assuming you have an ICON Controller, what is fire Service adjustment F16 set at?? If you are not in a state where there is some farout code deviation,IE Detroit, New York LA,etc., then it should be set at 13. The last number in the manual is 12, but there is a 13 and it is ANSI A17.1 2012 edition I think. You could also add a relay in the car station that is picked up when you go to hold and use NC contacts to open common to the door close buttons.
0=No Fire Service
1=Ansi-1993
2=Chicago Building Code
3=California
4=New York City RS18-1
5=Massachusetts
6=ANSI 1988
7=Houston
8=Michigan
9=B44
10=White Plains, NY
11=ANSI 2000
12=B44-2000

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
I tried all on my simulator and none allowed the door close button to function on phase 2 hold.

Joined: Nov 2009
Posts: 468
Journeyman
Journeyman
Joined: Nov 2009
Posts: 468
I don't have a print handy, could it be wired to an incorrect input?/ I tried the fire service on a two stop today and door close does not allow the door close to function.

Joined: Nov 2009
Posts: 468
Journeyman
Journeyman
Joined: Nov 2009
Posts: 468
In hold position

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
appreciate all the responses.... im up in MA so our codes are little crazy. its an IMPACT controller. pic attached.
Attachments
23 norfolk.jpg (865.33 KB, 71 downloads)

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
That is definitely not a Tac20... Nevermind

Joined: Nov 2009
Posts: 468
Journeyman
Journeyman
Joined: Nov 2009
Posts: 468
I would wire a relay to pick when you put the phase two switch in the hold position. Then use the contacts to disconnect the door close signal.

Joined: Nov 2009
Posts: 468
Journeyman
Journeyman
Joined: Nov 2009
Posts: 468
Is an Impact controller a Dover/TKE controller?

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Not one that I’ve ever seen.

Joined: Feb 2014
Posts: 19
R
stranger
stranger
R Offline
Joined: Feb 2014
Posts: 19
It looks like a Swift Meridia. There is a manual on Vertical Express website that looks similar to the CE/Swift ones.

Joined: Aug 2015
Posts: 46
Hazanko
Hazanko
Joined: Aug 2015
Posts: 46
I knew TK aquired CE but I didnt realize it was pre Futura. Worked on the 5000's, Meridias, and Futuras, but ive never seen one that looked like this. I remember them being Bluish Purple but everything , CPU , modules, and Contactors are all lined up exactly the same, is this still CE or is this a TK touch up?

Last edited by JHessorz; 03/14/20 02:15 PM.
Joined: Aug 2013
Posts: 35
M
newbie
newbie
M Offline
Joined: Aug 2013
Posts: 35
Please feel free to contact Issa Lwaysi from Miltronics Inc. @ (917) - 417 - 7389. We provide FREE Tech support for all CEC swift 5000, Futura, & Merida related equipment. 24/7 SUPPORT

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
johnny, not sure of the input, will definitely check it. not familiar at all with this product and the prints were snagged before we got in.

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
Troubleshoot it more today using the swift tool and wasn’t able to see anything in the program regarding it - tried on medical service and it works properly which tells me it’s more likely programming.

Anyone use the swift futura wizard? Wondering if there’s anyway to program an additional bit that says when input for fire phase 2 is on Hold position then DCB is disabled or something along those lines

Joined: Jan 2014
Posts: 736
R
old hand
old hand
R Offline
Joined: Jan 2014
Posts: 736
You can log in with hyperterminal at a 19,200 baud rate and do a BITD and see the states of bits, Set or Reset. You can also change them.

Last edited by Rolly; 04/24/20 05:19 PM.
Joined: Apr 2020
Posts: 520
Likes: 2
addict
addict
Joined: Apr 2020
Posts: 520
Likes: 2
Do you have a manual for the VE Impact?

Joined: Apr 2020
Posts: 520
Likes: 2
addict
addict
Joined: Apr 2020
Posts: 520
Likes: 2
ElevatorGuy128, I'm not seeing any F/S bit settings that would change anything with the door operation on F/S phase 2 hold. I believe I installed the 11th Impact in the country 10 years ago. VE discontinued them before we were done with the adjusting. One of the big 4 just modernized one in Helena. PM me for more info.

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
Montana I actually do have a VE Impact manual - went through it a bunch of times and wasn't able to see any setting that would account for this either.... spoke with a tech on the phone who has reviewing it but never got back to me. My thinking is that this has been like this all along but was only recently picked up...either that or the CNA board behind the COP could be damaged? We've been pushing them on a changeover but its a small two stop and its not used often so they don't see the point in spending the money

Page 1 of 2 1 2

Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24