Installing a hydraulic package with Virginia controller - job has single phase coming in so we have a phase technologies solid state phase converter, motor is nidec 230v.... running up the motor is loud as hell, and after about 6-8 seconds my overload trips. Triple checked wiring of the motor with my Mfg and see no issues. When running up and measuring voltage between legs I have a drop on one set that goes down from 240 to 175 and another set goes down to 215. Mfg is at a loss and electrician isn’t much help. My knowledge of electrical and motors is not too advanced so I’m stuck. Not sure if this is a motor problem causing it or incoming power from the phase converter? Appreciate any help or suggestions

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Is it running the right direction?

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
The motor should be inverter rated but that would most likely just affect longevity. I’ve never seen an inverter type phase converter on a hydro. Thyssen just uses capacitor start for single phase jobs. But the inverter on my mill runs the 3 phase motor beautifully. Lots of variables with inverters and single phase power though. What is the incoming voltage phase to phase? What is the model of the inverter?

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
so i spoke to a few techs on both the motor side and phase converter side. sitting idle i was seeing 240 leg to leg all around, as i ran up i had two drops to 175 and 215 which i thought may be part of the issue. Speaking to the Converter tech he said this is normal it seems because it looks like the motor is pulling too many amps and the phase converter is actually designed so that it drops voltage if greater than 130 amps are being pulled. The controller manufacturer is now having me rewire the Motor Overload relay so that the T3 leg to the motor essentially by passes the overload. Apparently they think the electronic overload is having issues because of the way the phase converter is providing the 3 phase power... or something along those lines. Doesn't make much sense to me, the motor is loud as all hell when running too but apparently they think rewiring this overload will correct that as well.

Joined: Aug 2016
Posts: 35
newbie
newbie
Joined: Aug 2016
Posts: 35
A static converter might need to be substantially oversized for the motor it's running. I ran into problems running my lathe and mill using a converter I made from scratch. I eventually bought an off-the-shelf rotary converter from Phase-a-matic. You might look at their web page for insight.

A buddy runs his lathe off a static converter that is apparently sized correctly, but his motor takes a long time to get up to speed. One more thing, if you're going to run computer equipment, you'll probably need to be oversized and then filter the output from the converter.

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
More updates - rewiring the overload did not change anything so now the controller manufacturer is sending a completely different type of overload to replace what is currently there.... they are thinking the current electronic overload is having issues with the 3 phase produced by the phase converter. So im currently awaiting a new overload....strange thing is i have the same set up on another new install i'm doing and did not have these issues....and when i say same set up i mean almost exactly the same. Same phase converter, same elevator controller and same motor, same overload in controller... makes me question the phase converter and how it is wired up at the job im having issues at (electrician there is not the greatest to put it lightly). will try to send an update when i change out that overload

Joined: Jun 2018
Posts: 102
E
member
member
E Offline
Joined: Jun 2018
Posts: 102
another update for those interested - no change, phase converter tech now sending a new board for the phase converter. Looking to be an issue with the converter not the elevator.

Joined: Apr 2020
Posts: 520
Likes: 2
addict
addict
Joined: Apr 2020
Posts: 520
Likes: 2
Thanks for the update. Keep us posted.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.037s Queries: 30 (0.014s) Memory: 3.0337 MB (Peak: 3.5931 MB) Data Comp: Off Server Time: 2026-09-21 08:59:05 UTC
Valid HTML 5 and Valid CSS