Wondering if anyone can jump in and help me with a TK LEV chain drive. Mfg date 07/10. Replaced the main board (blue, PN 2900102) after a lightning strike. I can call the car between floors 1 & 2 but it will not travel to floors 3 or 4 when I call via hall stations or the COP. When call buttons are pressed for floors 3 or 4 the led ring does light temporarily but it does not call or cause the gate to close. There are no fault codes and the interlocks are working correctly on all floors (elevator will not move between 1 and 2 if door is open on 3 or 4). Does the board need to be programmed with a tool via for more than 2 floors or does the presence of Hall Station and Door Lock wiring signal the number of available floors? All wiring was put back as original with hall station wiring in jacks 1-4 and interlocks in door jacks 1-4. Also have the Cat5 jumper wire between Door Lock Front jack 5 and Door Lock Rear jack 9 to complete the interlock string.