#31630 08/29/21 01:10 PM
Joined: Aug 2016
Posts: 778
J
old hand
old hand
J Offline
Joined: Aug 2016
Posts: 778
Hey guys and girls. Got a Tac 20 hydro 4 (b-3). stop. Car is in pit .. indicator says B. Siemens drive not lit up. No 110v to top f pin connector . Main line power good. Have 480v between each leg. Top of drive and bottom. IMS records no faults after a power reset . mut relay is energized . Car monitor says safeties .. The last faults recorded were 1058-1 (selector position wrong at limit of travel) .. 1043-1 (low oil shutdown ) .....1033-1 (selector position error ) ..1055-2 (Selector car position mismatch ) 1057-1 (encoder out of tolerance) .. 1017 (software error - change in run type during run . Car is not performing an emergency stop and the software has changed the type of run (leveling , stopped after a run , controlled full speed run , etc.. 1040 (door watch dog closing failure ) .. would the drive going bad cause these faults ? Shoukd I bring 120v to pin connector 1 on drive to see if it starts up and pulls in contactor ?

Jluff #31631 08/29/21 02:57 PM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Those position faults are likely from a power cycle. Common with the BP inputs over LON. TAC20s will drop MCC1 to turn off the starter with certain faults and if MUTS is picked with the starter off, the up to speed contact is probably shorted. You could probably break the C65 surface mount capacitor on the Logic Board. The fact that is says Safeties is interesting though, a TAC20 should only say that if you really don’t have safe.

Jluff #31635 08/29/21 11:55 PM
Joined: Mar 2011
Posts: 153
member
member
Joined: Mar 2011
Posts: 153
I'm with Indirt. C65 capacitor is shorted. Take the wire off of 5 or 6 on the Siemens starter then power up. If you get the right capacitor there is a C65B place to solder a new one on. Or is it C56? I can't remember.

Jluff #31660 09/01/21 11:29 PM
Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
I found on the newer logic boards they stopped putting the cap on the boards so now I just pull them off.

Jluff #31662 09/02/21 01:08 AM
Joined: Mar 2011
Posts: 153
member
member
Joined: Mar 2011
Posts: 153
Good to know. Thanks.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.161s Queries: 24 (0.122s) Memory: 3.0164 MB (Peak: 3.5926 MB) Data Comp: Off Server Time: 2026-09-20 21:14:07 UTC
Valid HTML 5 and Valid CSS