Got a Tac 20 hydro. When it starts up Siemens starter says motor up to voltage then low leg amp fault and contactor drops out and stater goes blank . My main line power is good. Motor sounds fine on start up. Any time I have seen these Siemens starters go blank screen they needed to be replaced. Has anyone seen this before ?

Joined: Feb 2014
Posts: 28
E
newbie
newbie
E Offline
Joined: Feb 2014
Posts: 28
Probably and issue with the starter itself, Have you called Siemens?

Joined: Dec 2015
Posts: 1,769
Likes: 12
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,769
Likes: 12
TAC20s will remove power to the starter on an init shutdown. If the motor tests good and you’re sure the 3 phase is solid, replace the starter.

Joined: Aug 2016
Posts: 778
J
old hand
old hand
J Offline
Joined: Aug 2016
Posts: 778
Replaced the starter now it stays on but motor is bad . Got two low legs and smoke coming from motor. There was Supposedly no power problems In the building.

Joined: Oct 2019
Posts: 1
D
stranger
stranger
D Offline
Joined: Oct 2019
Posts: 1
So, Im going through the same thing on a tac20. What ended up being the fix? I was having intermittent low leg faults too(every 3 months), then one night I walked in on the soft start off completely. Cycled power several times and it finally hooked up and let the car come down.

Joined: Aug 2016
Posts: 778
J
old hand
old hand
J Offline
Joined: Aug 2016
Posts: 778
Well my motor is bad. In the process of replacing it. You shoukd check your daily log on the starter. It will save the info for the last 3 faults. Look to see which legs are low. Then change your wire configuration at the bottom of the drive and at the fault contactor. Move each wire one spot to the left. So if it’s 1-2-3 at bottom of drive change it to 2-3-1. Do the same at fault contactor. If it’s 6-4-5. Change it to 4-5-6. Then when it happens again check the fault log on drive to see if the low legs moved with the new wire configuration. If they moved the same as wiring the motor is the problem. If they don’t change the drive is the problem.

Last edited by Jluff; 03/04/21 12:54 PM.
Joined: Aug 2021
Posts: 1
B
stranger
stranger
B Offline
Joined: Aug 2021
Posts: 1
Hi....At the point when you go out to attempt to begin it, will be it totally dead, or does it give a clicking sound and go dead, or does it simply wrench slow. In case you are doing a ton of investigating (beginning and halting the motor) and not getting a lot of run time, and in addition to if the motor is somewhat difficult to begin, I am contemplating whether this action might be depleting the battery low. What amount of time does it require before it goes dead?

Joined: Apr 2020
Posts: 522
Likes: 2
addict
addict
Joined: Apr 2020
Posts: 522
Likes: 2
Do you have the phone number for Siemens tech support?


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.36 Page Time: 0.072s Queries: 30 (0.029s) Memory: 3.0320 MB (Peak: 3.5920 MB) Data Comp: Off Server Time: 2026-11-05 12:45:11 UTC
Valid HTML 5 and Valid CSS