Joined: Aug 2021
Posts: 4
P
stranger
stranger
P Offline
Joined: Aug 2021
Posts: 4
Hey guys,
Anyone have answers to lowering/removing extreme static discharge when hotel guests hit the call buttons on the upper floors (floors 2-4) of a hotel? The elevator landing area as well as the corridors have carpet and in the winter months, it really gives a big static charge when guests hit the call buttons. It doesn't happen/not near as prevalent on the first floor as it's all tile in that area. We have one TKE Endura 35 II A and one TKE Endura 25 A MRL Hydraulic TAC32 elevators with standard stainless steel trim and stainless steel call buttons at each floor.

Joined: May 2020
Posts: 44
U
newbie
newbie
U Offline
Joined: May 2020
Posts: 44
You could ground every hall station to the building steel, or switch the buttons out with plastic ones, but they suck, had a problem like that years ago, we just grounded them to the duct work which was attached to the building steel

Joined: Nov 2009
Posts: 473
Journeyman
Journeyman
Joined: Nov 2009
Posts: 473
Grounding won't help. The faceplates and boxes should already be grounded. I think the biggest problem with static is low humidity. You might ask the maintenance if any thing could be done. I have the same problem in the wintertime in my own house.

Joined: Feb 2015
Posts: 81
B
journeyman
journeyman
B Offline
Joined: Feb 2015
Posts: 81
Another option that is commonly used on bronze buttons to prevent oxidization is a clear insulating conformal coating on the buttons.

Joined: Feb 2015
Posts: 81
B
journeyman
journeyman
B Offline
Joined: Feb 2015
Posts: 81
Might also want to apply to face plate as the static is discharging to ground. Ask your service mechanic.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
Unless the hall station is low voltage, you should not isolate it from ground.

Joined: Mar 2016
Posts: 270
Likes: 2
L
Elevator guy
Elevator guy
L Offline
Joined: Mar 2016
Posts: 270
Likes: 2
Had to add additional grounding on 2 jobs because I kept losing hnb cards with carpeted floors. Fixtures were bonded to the box only. This was mentioned by tech support after everything else was eliminated. Lost 2 cards in one week once. Problem went away after.

Joined: Feb 2022
Posts: 6
B
stranger
stranger
B Offline
Joined: Feb 2022
Posts: 6
Had the same problem , asked the customer to get the carpet sprayed with anti- static spray , it definitely helped


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.022s Queries: 30 (0.006s) Memory: 3.0314 MB (Peak: 3.5928 MB) Data Comp: Off Server Time: 2026-09-21 08:30:39 UTC
Valid HTML 5 and Valid CSS