I posted a different problem today with a fire service issue
2 stop unit, manual freight doors, main and alternate backwards.
I tried reprogramming them via the Omeron programmer. The main floor is the top(2nd) and alternate is the basement (1).
So per the book I have.
On the tool...
TRS,CNT,1,Read,2 enter :to set the main recall to 2nd floor

Then
TRS,CNT,2,Read,8 enter: to set the alternate floor.
Initially I used a 1 instead of the 8 here, but there is a note in the book saying on a two stop it has to be set at 7(top landing)
Either way the results were the same.
Car tries to recall to correct floor, stops at the floor then will run to the other floor. It continues to cycle like this. As far as I can tell I can view the IO info via the tool MON(add) function and they match what is on or off.
So, not sure if I am missing a step or might have a defective ee2 chip. It is an FA-2 junior unit with a 4k EE2 chip.module