#35530 07/18/23 02:20 AM
Joined: May 2015
Posts: 359
W
enthusiast
enthusiast
W Offline
Joined: May 2015
Posts: 359
I’m having a very intermittent problem with the car faulting out on a safety fault (F6) but have physically checked all safety devices as well as replaced the IO board and relays twice. Smartrise has not provided much help saying it is difficult troubleshoot such an intermittent issue. I have spent many hours on site running the elevator for hours with out it shutting down once. It a very odd issue and I think it might software related. Thanks

Joined: Aug 2017
Posts: 579
Likes: 6
E
addict
addict
E Offline
Joined: Aug 2017
Posts: 579
Likes: 6
I have one doing the same thing. Randomly stopping between floors. In either direction, any speed, any point in the hoistway. Will sit between floors for 30 seconds then take off again and run fine for hours or many days. Customer never calls it in, I've seen it happen being on another car doing PM and I check the fault log to see if it's still happening. Extra info A-M-3-0. Might run a week without it happening, might happen 6 times in one day.


I've moved SRU board inputs, replaced lock board (to updated version), replaced all the force guided relays, replaced the hookbill beak and door lock contacts in every lock, replaced gate switch contacts, adjusted clutch to pickup roller distance way big, replaced E brake pick switch, had rewired B and B2 contactors (to have contacts in parallel not series), swapped pick relay with the other car, swapped travel cable wires for safety string to spares.

Today I replaced the B and B2 contactors with brand new ones and also replaced the B2 contactor's aux contact and both aux contacts on the M contactor with new ones. We'll see how it goes.

Joined: Aug 2017
Posts: 579
Likes: 6
E
addict
addict
E Offline
Joined: Aug 2017
Posts: 579
Likes: 6
I have to check my log book. I think I may have replaced the MR SRU board too

Joined: Dec 2015
Posts: 56
Likes: 1
LA Elevator
LA Elevator
Joined: Dec 2015
Posts: 56
Likes: 1
I have heard from a former Smartrise engineer that the hardware design of the SRU board has some known flaws that make it overly sensitive to noise and slight increases in ambient and board temperature. These issues cause certain signals to change state in the circuit boards, leading to most of the intermittent problems experienced with Smartrise controllers. Unfortunately, there is currently no known fix for these issues.

Joined: Dec 2021
Posts: 55
Miami Elevator
Miami Elevator
Joined: Dec 2021
Posts: 55
I think that could explain why we get more of these intermittent safety faults in hot days.

Joined: Aug 2017
Posts: 579
Likes: 6
E
addict
addict
E Offline
Joined: Aug 2017
Posts: 579
Likes: 6
Yeah so the two B contactors and all the aux contacts weren't it either. Darn thing had stopped between floors twice in the last 24 hours.

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Man I’d put a data logger on it or at least set a couple traps in the safety circuit

Joined: May 2020
Posts: 44
U
newbie
newbie
U Offline
Joined: May 2020
Posts: 44
I had 2 problems with one smartrise doing this, the first was a loose wire on the car top SRU board, the 2nd was the traveling cable was hitting building steel, if that helps

Joined: May 2015
Posts: 359
W
enthusiast
enthusiast
W Offline
Joined: May 2015
Posts: 359
Update: I’ve never seen an elevator wired into a typical electric panel but it’s wired into a 90A breaker but has a minimum 96A rating and should really be at least 125A minimum when starting up.
Drive is HPV900 and is logging Phase loss when Controller is logging F6 Safety String. Extra bytes are 1-0 indicating potential issue with M1 contractor.
We’re going to address/correct breaker issue first and then go from there.

Joined: Dec 2015
Posts: 56
Likes: 1
LA Elevator
LA Elevator
Joined: Dec 2015
Posts: 56
Likes: 1
@wltr00, any updates on this? Did changing the breaker fix the intermittent safety fault issue ?


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.025s Queries: 34 (0.008s) Memory: 3.0438 MB (Peak: 3.5926 MB) Data Comp: Off Server Time: 2026-09-20 22:50:19 UTC
Valid HTML 5 and Valid CSS