1155 fault is MCD active and MCE active after MCC outputs fire:possible failures: (1) old generic software, resolution: update generic software to v4r5p, where possible. (2) loose connection in MCD circuit, resolution: check all wiring. (3) Bad input, resolution: replace IOA for tac20-03 or 188e tac22/tac20 (4) up run stall timer, Z35, set to low, resolution: increase Z35 adjustment.

If this helps, it's the info I had.on your fault at least.