Hey guys, I have a intermittent problem with a swift futura. It's getting stuck doors open with faults 104,105 and 109. I am noticing that only when the car goes UP the LED'S named: COMM and FLT become yellow on the COP,Cpt and TOCC (or red, sometimes). This is pretty consistent in the up direction, however in the down direction I have not noticed any changes.

**Watching from the RVU-Wizard display**

Sequence of activation of LED:
1- WHEN AT LEVELING The "COM" led turns yellow on the TOCC
2- Then, on the COP "COM" Led turns yellow
3-Finally on the CPT the "COM" LED turns yellow(Sometimes while turning yellow on CPT it also turns red and randomly it can shutdown on a DZ fault!!!).

All this happens only when the Leveling sequence starts.

What does the yellow color on Comm means? No fault occurred while doing this issue but of course I get a call back everyday.

Replaced:
1- CPT
2-UFLZ,MLZ,DFLZ sensors
3-CPU-Link
4-Cable that goes from the CPT "DZ" signal to CPU-link board.
5- Capacitor MC
6- MC,BK,SM contactors(previous issue)
7-Selector guides

Adjusted:
1-Power supply voltage at 24.800VDC at pot, receiving 23.800VDC-24.00VDC at DZ terminal on CPU-Link

Unit: Swift Futura, 1995


Thank you