So today changed out all limit tree switch's except one did not have but verified it was working.changed out top of car inspection switch ,changed out selector card and auxiliary sensor card .still have issues .when running from top of car at 1st floor put on INSPECT IN relay drops in controller attempt to run up IN relay picks in controller and immediately runs back down to floor level.Is IN relay supposed to pick during inspection run ? You can also see this on laptop CLC/variables IN goes from red to blue changing state is this correct? The one thing I have to look at is the installation of the main sensor card I was not present when that was installed can that be installed wrong direction or orientation I have never done one of these so Im not sure have to verify that could something like this create this issue again I'm not sure.