We are doing a mod on a Kone duplex with TMS600 controllers circa 1995 and need to divorce Car 2 from Car 1. All of the interconnections between the controllers were being removed but when the interconnections for the fire detectors from M2/1, M2/2, M2/3 from Car 2 are removed, Car 1 goes onto fire service. The interconnections just go to the inputs B/18A, B/16C, and B16E, on both boards. Why would removing the inputs from Car 2 controller set off the fire service on Car 1? They are just paralleled. Do they need termination resistors, etc.