If you place the controller on inspection fault bypass (F3 menu) you should be able to move if the safety circuit is made up and doors are locked. Unless you have the door bypasses on. F7 parameters are stored on the MPI board and the F1 settings are stored on the CPU board. If you go into the F3 menu and the controller system menu then look at the Elgo A and B channels. They should both increment as you move up and down the hoistway. If they don’t you either have a canbus wiring issue or bad tape reader. Also make sure you have power to the Elgo from the LSI board. Check those and let us know what you find.