Hi Guys,
We have a Kone Eco 5 floor in the UK that's stopping out of level, its running by in both directions to varying degrees at all floors and then levelling to correct level.
G 5mm Low
1st Ok Down 60mm high up
2nd 30mm low down & 70mm high up
3rd 70mm low down and similar high up
4th 5mm low down and ok up
5th ok
We have checked the LWD all ok re-setup to be sure, checked magnet arrangement all ok nothing moved, replaced all proximity switches, replaced tacho and had drive tested on a Kone test rig.
carried out a shaft learn, Lon download numerous times and just cant get it it to stop level......
Any ideas appreciated as we are running out of them, P.S no rope slip, checked for that, guides are well lubricated, and we seem to be getting all the correct signals and NO ERRORS showing ? mad: