elmcannic Thanks.
Doesn't move from 1. Maybe a few inches. MUTS never comes in. Doesn't go on in up slow to intended floor. And IMS logs no fault?????
Only does it when hot or warm. If oil were to stay cool, it would keep running (long story but tested this). It does re level once in a while which is pointing to check valve(s) (man have we done alot of these check valves and have more lined up)
Bucher tool set on #3 at .02 (supposed to be within tolerance / hall sensor feedback). But now other techs are telling me that how tight the tank lid is affects this??? If something is that temperamental it shouldn't be in any elevator. Looked it up its true.
The last 3 faults are now this: 2766 1684 1170 in order (node comm, node comm loss or potential power supply, low pressure jack inhibiting down run). But my 20+ years doing this the 1170 caused it and the other two were the result in descending / ascending order whatever. But not sure how low pressure would cause comm errors.