Picked up a dover LMH 3 stop hydro on my route, never seen one before. Anyone have any experience with these?
|
|
|
|
|
Joined: May 2011
Posts: 338
Mechanic
|
|
Mechanic
Joined: May 2011
Posts: 338 |
If it has the plc I think they are a fairly decent controller. Parts for these are still available though vertical express or TKE I believe. If it is the earlier non PLC version your in trouble as far as parts and support.
|
|
|
|
|
Joined: May 2012
Posts: 194
member
|
|
member
Joined: May 2012
Posts: 194 |
...I have been maintaining this equipment for awhile at present time I have 6 and they are all 5-stop freights w/peelle doors..have never encountered any problems with this equipment ..work horses..
|
|
|
|
|
Joined: Sep 2012
Posts: 451
addict
|
|
addict
Joined: Sep 2012
Posts: 451 |
Well this is good news. There is some sort of service tool that was in the machine room. Hopefully ITS can send me some manuals soon.
|
|
|
|
|
Joined: Nov 2013
Posts: 23
stranger
|
|
stranger
Joined: Nov 2013
Posts: 23 |
5 volt power supply for logic, and two main logic boards, a relay board and logic board, these baby's are expensive. The relay board has the field wiring terminals and can be found on the prints. It comes down to your control voltage, P24, being pulled to ground with the logic board to initiate a circuit. If you can get a manual, they have pin identification for signals on the chips and drivers. and a manual has a set of prints in it hopefully.
Last edited by mjm; 11/03/13 03:42 AM.
|
|
|
|
|
Joined: Jun 2013
Posts: 72
journeyman
|
|
journeyman
Joined: Jun 2013
Posts: 72 |
Sbrmilitia have your supervisor get on TNET there are LMH manuals on there
The tool is to program I/O information in the PLC and set parameters That is explained in the manual
|
|
|
|
|
Joined: May 2012
Posts: 194
member
|
|
member
Joined: May 2012
Posts: 194 |
The tool is a Idec programmer..have not had any eprom issues with this equipment..find it very reliable
|
|
|
|
|
Joined: Sep 2012
Posts: 451
addict
|
|
addict
Joined: Sep 2012
Posts: 451 |
I got some info off of T net for it. Haven't had any issues with this car yet. This car runs constantly and only a few door calls. Next to my DMCs one of the better running cars I have on my route full of junk.
|
|
|
|
|
Joined: Dec 2013
Posts: 1
stranger
|
|
stranger
Joined: Dec 2013
Posts: 1 |
Any one have board prints for a lmh . Have one that fire recall isnt working properly. when you run up on phase 2 and turn the key in car to normal car will not return to fire recall floor
|
|
|
|
|
Joined: Sep 2012
Posts: 451
addict
|
|
addict
Joined: Sep 2012
Posts: 451 |
|
|
|
|
|
Joined: Nov 2009
Posts: 473
Journeyman
|
|
Journeyman
Joined: Nov 2009
Posts: 473 |
Problem is in the software. Thats what the programmer is for. Changing the software without the program is not for the faint of heart. What version of software is in the controller? It will be printed on the program chip. Should be something like 8LILH. This means up to eight landings in line hydro. With the programmer, you can copy the program into another Ram pack and then experiment with the duplicate and not mess up the original programming.
|
|
|
|
|
Joined: Nov 2009
Posts: 473
Journeyman
|
|
Journeyman
Joined: Nov 2009
Posts: 473 |
I said that the problem is in software, but I am assuming that all inputs are correct when you have this problem. Also, check your code date and see whether or not the code addressed this condition before you change anything.
|
|
|
|
|
Joined: Jan 2012
Posts: 419
addict
|
|
addict
Joined: Jan 2012
Posts: 419 |
I said that the problem is in software, but I am assuming that all inputs are correct when you have this problem. Also, check your code date and see whether or not the code addressed this condition before you change anything. IDEC's you can download ladder logic, but no labels if you don't have the source code. In other words you download, look at a bunch of contacts, coils, timers, counters, but you have no clue what they do because you don't have any labels.... That is unless you have the source coded.
|
|
|
|
|
Joined: Nov 2009
Posts: 473
Journeyman
|
|
Journeyman
Joined: Nov 2009
Posts: 473 |
I have the labels for certain LMH programs, thats why I ws asking which version he has.
|
|
|
|
|
Joined: Feb 2013
Posts: 21
stranger
|
|
stranger
Joined: Feb 2013
Posts: 21 |
Have the same problem on one of mine I have to run it down to recall floor before it will return to normal
|
|
|
|
|
Joined: Jan 2014
Posts: 432
addict
|
|
addict
Joined: Jan 2014
Posts: 432 |
this is how the circuit works in many of the older cars, the car stays on phase 2, with the key switch in the off position if the car is at any landing other the the main. at least in california this is how it works, tested many of them and had to test that circuit also. removed the key and made sure it stayed on phase 2. it only clears phase 2 when at main landing and door fully open.
|
|
|
|
|
|
|
|
|